Mitsubishi Error Code Check
admin@admin
10 Posts
#1 · January 17, 2025, 10:37 am
Quote from admin on January 17, 2025, 10:37 amhttps://youtu.be/RzN3z3i2ISg
Model Number:
- MSY-GJ13VA
Step 1:
Press "Too Cool" + "Mode" + "Reset"
Step 2:
Release "Reset" & Hold "Too Cool" + "Mode" foc 3 sec
Step 3:
Point the remote to that air cond and press "ON" button
Step 4:
Heard and calculation the "beep" sound
Upper Lamp Of Operation Indicator Lamp Abnormal point
(Failure mode)Condition Not lighted Normal None (Normal) 1-time flash every 0.5 second Room temperature thermistor Room coil temperature thermistor is short/open circuit 2-time flash, 2.5 second OFF Indoor coil thermistor Indoor coil temperature thermistor is short/open circuit 3-time flash, 2.5 second OFF Serial signal Rotation frequency feedback signal is not emitted during the indoor fan operation 4-time flash, 2.5 second OFF (Inverter only) Indoor fan motor Indoor PCB failure 5-time flash, 2.5 second OFF (Inverter only) Indoor control system Compressor stops after 3 times of over-current / start-up failure protection within 1 minute after start-up 6-time flash, 2.5 second OFF (Inverter only) Outdoor thermistors Outdoor thermistor is short / open circuit 7-time flash, 2.5 second OFF (Inverter only) Outdoor control system Indoor / outdoor PCB failure 11-time flash, 2.5 second OFF Indoor fan motor Rotation frequency feedback signal is not emitted during 12 seconds the indoor fan operation 14-time flash, 2.5 second OFF Refrigerant circuit
Unit has been pump down for a long time Refrigerant amount is low Unit is short cycling Outdoor fan motor locks up
Model Number:
- MSY-GJ13VA
Step 1:
Press "Too Cool" + "Mode" + "Reset"
Step 2:
Release "Reset" & Hold "Too Cool" + "Mode" foc 3 sec
Step 3:
Point the remote to that air cond and press "ON" button
Step 4:
Heard and calculation the "beep" sound
Upper Lamp Of Operation Indicator Lamp | Abnormal point (Failure mode) |
Condition | ||||
---|---|---|---|---|---|---|
Not lighted | Normal | None (Normal) | ||||
1-time flash every 0.5 second | Room temperature thermistor | Room coil temperature thermistor is short/open circuit | ||||
2-time flash, 2.5 second OFF | Indoor coil thermistor | Indoor coil temperature thermistor is short/open circuit | ||||
3-time flash, 2.5 second OFF | Serial signal | Rotation frequency feedback signal is not emitted during the indoor fan operation | ||||
4-time flash, 2.5 second OFF (Inverter only) | Indoor fan motor | Indoor PCB failure | ||||
5-time flash, 2.5 second OFF (Inverter only) | Indoor control system | Compressor stops after 3 times of over-current / start-up failure protection within 1 minute after start-up | ||||
6-time flash, 2.5 second OFF (Inverter only) | Outdoor thermistors | Outdoor thermistor is short / open circuit | ||||
7-time flash, 2.5 second OFF (Inverter only) | Outdoor control system | Indoor / outdoor PCB failure | ||||
11-time flash, 2.5 second OFF | Indoor fan motor | Rotation frequency feedback signal is not emitted during 12 seconds the indoor fan operation | ||||
14-time flash, 2.5 second OFF | Refrigerant circuit |
|