Quote from
admin on January 17, 2025, 10:37 am
https://youtu.be/RzN3z3i2ISg
Model Number:
- MSY-GJ13VA
Step 1:
Press "Too Cool" + "Mode" + "Reset"
Step 2:
Release "Reset" & Hold "Too Cool" + "Mode" foc 3 sec
Step 3:
Point the remote to that air cond and press "ON" button
Step 4:
Heard and calculation the "beep" sound
| Upper Lamp Of Operation Indicator Lamp |
Abnormal point
(Failure mode) |
Condition |
| Not lighted |
Normal |
None (Normal) |
| 1-time flash every 0.5 second |
Room temperature thermistor |
Room coil temperature thermistor is short/open circuit |
| 2-time flash, 2.5 second OFF |
Indoor coil thermistor |
Indoor coil temperature thermistor is short/open circuit |
| 3-time flash, 2.5 second OFF |
Serial signal |
Rotation frequency feedback signal is not emitted during the indoor fan operation |
| 4-time flash, 2.5 second OFF (Inverter only) |
Indoor fan motor |
Indoor PCB failure |
| 5-time flash, 2.5 second OFF (Inverter only) |
Indoor control system |
Compressor stops after 3 times of over-current / start-up failure protection within 1 minute after start-up |
| 6-time flash, 2.5 second OFF (Inverter only) |
Outdoor thermistors |
Outdoor thermistor is short / open circuit |
| 7-time flash, 2.5 second OFF (Inverter only) |
Outdoor control system |
Indoor / outdoor PCB failure |
| 11-time flash, 2.5 second OFF |
Indoor fan motor |
Rotation frequency feedback signal is not emitted during 12 seconds the indoor fan operation |
| 14-time flash, 2.5 second OFF |
Refrigerant circuit |
| Unit has been pump down for a long time |
| Refrigerant amount is low |
| Unit is short cycling |
| Outdoor fan motor locks up |
|
Model Number:
- MSY-GJ13VA
Step 1:
Press "Too Cool" + "Mode" + "Reset"
Step 2:
Release "Reset" & Hold "Too Cool" + "Mode" foc 3 sec
Step 3:
Point the remote to that air cond and press "ON" button
Step 4:
Heard and calculation the "beep" sound
| Upper Lamp Of Operation Indicator Lamp |
Abnormal point
(Failure mode) |
Condition |
| Not lighted |
Normal |
None (Normal) |
| 1-time flash every 0.5 second |
Room temperature thermistor |
Room coil temperature thermistor is short/open circuit |
| 2-time flash, 2.5 second OFF |
Indoor coil thermistor |
Indoor coil temperature thermistor is short/open circuit |
| 3-time flash, 2.5 second OFF |
Serial signal |
Rotation frequency feedback signal is not emitted during the indoor fan operation |
| 4-time flash, 2.5 second OFF (Inverter only) |
Indoor fan motor |
Indoor PCB failure |
| 5-time flash, 2.5 second OFF (Inverter only) |
Indoor control system |
Compressor stops after 3 times of over-current / start-up failure protection within 1 minute after start-up |
| 6-time flash, 2.5 second OFF (Inverter only) |
Outdoor thermistors |
Outdoor thermistor is short / open circuit |
| 7-time flash, 2.5 second OFF (Inverter only) |
Outdoor control system |
Indoor / outdoor PCB failure |
| 11-time flash, 2.5 second OFF |
Indoor fan motor |
Rotation frequency feedback signal is not emitted during 12 seconds the indoor fan operation |
| 14-time flash, 2.5 second OFF |
Refrigerant circuit |
| Unit has been pump down for a long time |
| Refrigerant amount is low |
| Unit is short cycling |
| Outdoor fan motor locks up |
|