Model Number:
- MSY-GJ13VA
Step 1:
Press "Too Cool" + "Mode" + "Reset"
Step 2:
Release "Reset" & Hold "Too Cool" + "Mode" foc 3 sec
Step 3:
Point the remote to that air cond and press "ON" button
Step 4:
Heard and calculation the "beep" sound
| Upper Lamp Of Operation Indicator Lamp | Abnormal point (Failure mode)
 | Condition | 
| Not lighted | Normal | None (Normal) | 
| 1-time flash every 0.5 second | Room temperature thermistor | Room coil temperature thermistor is short/open circuit | 
| 2-time flash, 2.5 second OFF | Indoor coil thermistor | Indoor coil temperature thermistor is short/open circuit | 
| 3-time flash, 2.5 second OFF | Serial signal | Rotation frequency feedback signal is not emitted during the indoor fan operation | 
| 4-time flash, 2.5 second OFF (Inverter only) | Indoor fan motor | Indoor PCB failure | 
| 5-time flash, 2.5 second OFF (Inverter only) | Indoor control system | Compressor stops after 3 times of over-current / start-up failure protection within 1 minute after start-up | 
| 6-time flash, 2.5 second OFF (Inverter only) | Outdoor thermistors | Outdoor thermistor is short / open circuit | 
| 7-time flash, 2.5 second OFF (Inverter only) | Outdoor control system | Indoor / outdoor PCB failure | 
| 11-time flash, 2.5 second OFF | Indoor fan motor | Rotation frequency feedback signal is not emitted during 12 seconds the indoor fan operation | 
| 14-time flash, 2.5 second OFF | Refrigerant circuit | 
| Unit has been pump down for a long time |  
| Refrigerant amount is low |  
| Unit is short cycling |  
| Outdoor fan motor locks up |  | 
Model Number:
- MSY-GJ13VA
Step 1:
Press "Too Cool" + "Mode" + "Reset"
Step 2:
Release "Reset" & Hold "Too Cool" + "Mode" foc 3 sec
Step 3:
Point the remote to that air cond and press "ON" button
Step 4:
Heard and calculation the "beep" sound
| Upper Lamp Of Operation Indicator Lamp | Abnormal point (Failure mode)
 | Condition | 
| Not lighted | Normal | None (Normal) | 
| 1-time flash every 0.5 second | Room temperature thermistor | Room coil temperature thermistor is short/open circuit | 
| 2-time flash, 2.5 second OFF | Indoor coil thermistor | Indoor coil temperature thermistor is short/open circuit | 
| 3-time flash, 2.5 second OFF | Serial signal | Rotation frequency feedback signal is not emitted during the indoor fan operation | 
| 4-time flash, 2.5 second OFF (Inverter only) | Indoor fan motor | Indoor PCB failure | 
| 5-time flash, 2.5 second OFF (Inverter only) | Indoor control system | Compressor stops after 3 times of over-current / start-up failure protection within 1 minute after start-up | 
| 6-time flash, 2.5 second OFF (Inverter only) | Outdoor thermistors | Outdoor thermistor is short / open circuit | 
| 7-time flash, 2.5 second OFF (Inverter only) | Outdoor control system | Indoor / outdoor PCB failure | 
| 11-time flash, 2.5 second OFF | Indoor fan motor | Rotation frequency feedback signal is not emitted during 12 seconds the indoor fan operation | 
| 14-time flash, 2.5 second OFF | Refrigerant circuit | 
| Unit has been pump down for a long time |  
| Refrigerant amount is low |  
| Unit is short cycling |  
| Outdoor fan motor locks up |  |